Ok so here goes with another long post. I got an okay to share some details about a process chiller we built for condensing CO2 at -24F; I guess we all realized that we have no interest in selling chillers outright and hopefully someone rips off the design so we can just buy one lol.

Capacity is approx 80k btu at -24F, but it obviously can run colder. We’ve ran it down to -60F and then it started freezing the glycol.

The low stage:
We used a Copeland ZO88KCE to pump r744 (CO2). I can’t tell you our cost but I think retail is around $3k. Unfortunately, despite being a freaking awesome refrigerant, they’re not real common so the Americans at least won’t be able to find them used/new old stock.

The evaporator heat exchanger is a duda brazed plate, I think it’s a 60 plate 4x24" but I don’t remember exactly. They’re so cheap, just oversize it. We use the exact same HX for the interstage heat exchanger too but again, only because it’s oversized.

Expansion valve is a sporlan SER-C; sporlan will tell you that you only need an SER-B because of the pressure drop allowed but that is a crock of shit, ate a whole rev number for us lol. Depending on who’s building it you can run it off their Kelvin II superheat controller or you can run it off your own PLC. A little note here: the stock temp transmitter only goes to -60F and below that the controller will close the valve, blowing all your refrigerant and oil out the relief valve if you don’t address your logic accordingly; you’ve been warned. For lower temp operation, a mechanical TXV might be better but it will probably hunt like a mofo because there is not a product designed for these temperatures at this size.

We did not need a fade out tank because of how much evaporator piping we had, but there’s little downside to having one. I HIGHLY recommend wiring an unloader valve to run between the discharge (before the condenser) and suction of the evaporator to keep it from spiking pressure on startup because you will obviously want to keep the condenser-side volume as low as possible (this will mitigate the standstill pressure issue). You will also want a HP and LP cutout obviously, but you also need a pressure switch to ensure the low stage is sufficiently cold before it starts; this is much more effective than using a temp transmitter to do the same.

Now, this low stage hasn’t been “ratified” by Copeland but with our parameters it was well within their operating envelope. However, as you try to run this colder, oil management may become an issue which I have yet to address. Builder beware.

Pretty much all condenser piping is .035 wall 5/8 OD 304l welded, all evaporator piping is 1-1/8 OD of the same. The mueller HP copper can also do the pressure but it was waaaayyy more expensive than the stainless. Relief valve is set for 750 psi, service valves are where they always are.

High Stage:

We ran a ZPT166KCE tandem r410a compressor for the high stage. This allowed us additional capacity that we actually used as a dryer for the system air compressor. This is a much more common compressor with plenty of cross options.

Evaporator has been discussed already. For the condenser we used two 4-5 ton rated goodman slab coils. TXV sized out as a ERZE-6. Same deal with all the piping as the low stage, stainless is cheaper than the HP copper so, yeah, we did that.

Unloader circuit is helpful for the high stage as well if you don’t want to run a liquid accumulator.

We charged for the interstage to be operating around 32F so that you could visually see which stage was “winning”. If you bumped that up a bit, you could eliminate the entire high stage by using the facility chilled water (if it’s an option) which is usually around 44F. The next thing to do would be an R23 or N2 “even lower” stage but I haven’t had any time to select components for that.

If anyone has specific questions let me know. I can draw up a PID if y’all like but it’s probably not necessary for anyone that actually plans to build one. Total parts cost will probably come out in the $6-7k range, but could be quite a bit lower for a smart shopper/scrounger. It’s enough to condense 4+ kg/min of CO2 at -24F so it’s a pretty big unit.

12 Likes

Awesome write up thanks for taking the time. Gets me excited.

3 Likes

Of course there’s already a thread about this, lol.

We’re currently looking at picking up a bizzybee system and it would be the first rig I’ve ever run using LCO2. We also happen to have an Apex 25L CO2 machine just sitting around collecting dust. I see a lot of talk on this thread about utilizing the CO2 in a more traditional chiller method, but would you not be able to just inject the LCO2 from one bottle into the jackets and hook up the Apex diaphragm pump to the exhaust from the jackets to pump into an empty bottle? Or are there pressure issues that I’m missing here with how fast the CO2 could be pumped out of the jacket before it over-pressurized?

1 Like

As pointed out above, using a valve to create pressure drop and then using a pump to compress it so that it condenses is just a regular vapor compression cycle. You would need cooling to actually condense the CO2 with liquid and bing bam boom, you’ve created a chiller

2 Likes

Hmm. Well, the Apex is already set up with a jacketed column, but I’m guessing that wouldn’t provide the most efficient surface area for cooling. I’ll do some homework this week and talk to a friend of mine who’s well versed in HVAC and this Apex machine and report back, because I feel like I’m not well enough versed in this area to even ask intelligent questions yet. Good to have a thread to put me on the right track though. Been missing this community lately. :heart:

3 Likes

We’re happy to see you back around here. I didn’t mean to say that you can’t use you apex as a chiller because it’s pretty nearly that already. It’s just obviously not the most economical approach to making a chiller that uses CO2. The Copeland ZO series compressors exchanging to a regular split system AC or a building chilled water system can be pretty badass for several tens of thousands of dollars less than even the cheap second hand apex units.

1 Like

Copeland ZP series?

1 Like

ZP is rated for I think 600 psig for r410a, which is just a little on the low side for CO2. The ZO series is built for transcritical CO2 applications so they’ll do 1000 psig or so. They’re “the tits” for low stage on cascade systems.

4 Likes

I wish I could just pay you to come out and build one for me. Your understanding on this hard to find

5 Likes

I’ve seriously considered giving up “the big bucks” to be a roving refrigeration dude because I find it wicked fun lol. I haven’t made much progress on my mega chiller thread but I promise to share the chiller for the people when I get back to that project.

I think understanding of refrigeration systems is going to be one of these things like running SPD or a closed loop that this community will make pretty standard in the near future. Especially since the principles are very similar to running hydrocarbon systems already.

8 Likes

I understand the basics but without enough experience I think I’ll just waste my time trying to build a custom chiller without someone smarter than me moving the project forward. It’s like trying to do the digital work for packaging stickers and then somehow figure how to print batch information in the exact right spot.

I can do a lot of things, but I definitely know when to stay in my lane.

4 Likes

It’s kind of one of those things that you have to fuck up once or twice and then you know lol. I always love teaching people things, maybe one of these days I’ll grab a pile of parts and throw a little chiller building shindig.

Also, once I put that BOM and PID together, it’s going to be like paint by numbers. Somewhere I put up some details on the cascade 410/744 chillers we built. Not the same level of detail but the design is mostly there already, it’s basically just putting the parts together in the right order

6 Likes

I’ve made a couple chillers for clients. It’s alot easier than you think. You can buy the complete compressor section or build it. I used a simple metering txv and a stainless coil in a bath how cold you want to go?

4 Likes

I want to have around 18-20kw available at -60c

4 Likes

Injection and recovery I assume?

2 Likes

Yes
1 counter flow coil for injection
8-6x48 columns
1 200L recovery tank
1 4x48 shot gun condenser
1 10x12 shot gun condenser

1 Like

The 200l turning to a 400l with time?

1 Like

I have 2 200 liter tanks, but I only got my recovery tank with a jacket.

Fucked up there for sure

I can’t have more than 150lbs of fuel in the lab so I’m trying to device a plan to have 3-400lbs of already distilled fuel sitting outside in a few stainless dot tanks. Then I’d like to (if the fire Marshall will let me) run a hard line into the room so I can go make a quick connection and fill up my tanks again.

2 Likes

Just wheel them in after inspection.
I have 250 lb tanks delivered. I bring them in to top off system whenever needed.