Have never had an issue till last week. I had someone in there replacing hoses and when I turned it on next I started getting fault codes and my booth fans flipping to 100%.
Any help or thoughts on this would be greatly appreciated.
Hey there. Looks like the gas detector that is interlocked to the HAL panel safety features is in need of calibration. They drift over time and if it’s reading in the negatives at all it means you likely have a baseline error. i would call the company and ask for a rep to come calibrate. In the meantime, if you have one of honeywell’s magnet tools, you can interact with the interface and reset your baseline to 0.
You can also go into the HAL panel’s settings and change the trigger points for when the fan speed doubles. This may make the booth operational in the meantime.
@Distillight I have had this W006 error before. It is a “Latching” issue for the internal connection on the transmitter. If there is no solvent in the area, take off the gray cover and on the XNX transmitter, you’ll see a brass connection on the top and the bottom. Ensure they are seated properly, retighten the gray cover and then do a bump test. The code should clear.