Hey everyone. The cultivation facility at a company I work with has a grow in downtown LA. They have recently gotten hit with some code about an exhaust system for CO2 in their grow room. They were given a crazy 7 figure quote for a system to do this on their existing grow rooms. Anyone else have to deal with this?
Looking for recommendations of people anyone here has worked with in the LA area on this type of thing.
Here are the requirements listed in the code.
Gas Detection System: A continuous gas detection system shall be provided in the room or indoor area in which the CO2 enrichment process is located, in the room or indoor area in which the container systems are located and in other areas.
where CO2 is expected to accumulate, including rooms or areas directly adjacent to the enrichment area connected by doors or other means of travel. CO2 sensors shall be provided within 12 inches of the floor in the area where the gas is expected to accumulate or where leaks are most likely to occur. The
system shall be designed as follows:
- Activate a low-level alarm upon detection of a CO2
concentration not to exceed 5,000 ppm per CFC. - Activate a high-level alarm upon detection of a CO2
concentration not to exceed 30,000 ppm per CFC.
g. System Activation:
- Activation of the low-level gas detection system alarm
shall automatically:
a) Stop the flow of CO2 to the piping system.
b) Activate the mechanical exhaust ventilation
system.
c) Activate an audible and visible supervisory alarm
signal at an approved location within the building. - Activation of the high-level gas detection system alarm
shall automatically:
a) Stop the flow of CO2 to the piping system.
b) Activate the mechanical exhaust ventilation
system.
c) Activate an audible and visible evacuation alarm,
both inside and outside of the CO2 enrichment
area, and the area in which the CO2 containers
are located.
i. Pressurization and Ventilation: Rooms or indoor areas, in which CO2 enrichment is provided, shall maintain at a negative pressure in relation to the surrounding areas in the building. A mechanical ventilation system shall be provided in accordance
with the California Mechanical Code that complies with all of
the following:
- Mechanical ventilation in the room or area shall be at a rate of not less than 1 cubic foot per minute per square
foot. - When activated by the gas detection system the
mechanical ventilation system shall remain on until
manually reset. - The exhaust system intakes shall be taken from points
within 12 inches of the floor. - The ventilation systems piping shall terminate outdoors in an approved location.
- The pressure differential system and the ventilation
system shall be interlocked to the CO2 enrichment
system. Failure of either the pressure differential system or the ventilation system shall immediately result in the shutdown of the CO2 enrichment system.
Anyone else going through this currently? I guess if they can’t deal with it quickly it is going to require them stopping using CO2 which would be a big blow.