Vfd is the nicest option for it gives you some pump control as well
Any transformator can get a higher voltage conected
Yust make sure you have enough amp on the transfomator for the pump
And on the breaker switch from the socket
Feel free to reach out if you need a hand, if you’d like I can walk you through it or I could even put the drive in an enclosure with a twist lock outlet for the 3ph output and ship it to you.
Something is wrong with this ad.
750 watt power consumption is only about 3/4 horsepower.
Maybe is should read 7.5 kW power consumption.
That would be close to 10 hp which is about right for this size pump.
Also this is about where 240/3 phase is preferred…
You can only get 3 phase in your shop if it is wired for it from the pole to your box, otherwise a VFD is the ticket.